FCC Emergency Interlock System

Home Forums CatCracking FCC Safety FCC Emergency Interlock System

This topic contains 0 replies, has 1 voice, and was last updated by  Mrityunjay Singh 7 years, 9 months ago.

  • Author
    Posts
  • #1736

    Mrityunjay Singh
    Participant

    In the LinkedIn CatCracking Group
    Christian Argiolas asks:
    For catalyst slide valves electro-hydraulic actuating systems, the licensors specify to include 2 Solenoid valves in 2oo2 configuration for the ESD function (both de-energized to trip). For this solenoid valves it is specified to provide a proof test circuit that allows to verify the solenoid functioning without affect the position of the slide disc. The proof testing function is very important, it permits to verify periodically that both solenoid valves are ready to perform the ESD action. If one solenoid is stuck energized it won’t be possible to perform the ESD action. It is very important to detect this dangerous failure before the ESD demand, otherwise the actuator won’t be capable to perform the ESD action. How often do you perform the solenoids proof test for your slide valves?
    Read the replies and contribute to the conversation at http://linkd.in/YAgOes
     