RE: Interlocks and Actuator Control Philosophy – Looking for Advice….

Home Forums Coking Safety Safety Interlocks, Automation, Fire Suppression Safety Interlocks Interlocks and Actuator Control Philosophy – Looking for Advice…. RE: Interlocks and Actuator Control Philosophy – Looking for Advice….

#6089

Mitchell Moloney
Participant

Craig –
 
You need to have interlock/PLC signal power and motor operator power separate.  We deenergize and lock out the MOV’s at a breaker panel on the structure to protect the open drum from receiving hydrocarbon inadvertently.
 
I would also recommend not doing a sequence based interlock logic, if that is what you are inferring.  I recommend that each valve have a unique relationship with 2 or 3 other valve positions; those valves must be in their proper postion (closed, open, not closed or not open) as a permissive for moving the given valve to the desired position.
 
Best regards – Mitch